I have a Dyana that in using just the RF in tracing mode hooking up to the lost conductor will drop the signal off about 6" when I pass the bad section and if I mark it where I loose the signal, then turn around and trace it back from the other direction again it will drop off about 6" past the break, mark and directly between these two marks is the break, but why when I have the fault locater attachment for the Dyna? it hits it dead on.
I have a Dynatel earth return fault locator and cable locator also. (model 573A) IMO the best fault locating machine ever for finding secondary faults with the A frame.
Not much good for finding primary faults in 35 kV cable. These don't fault to earth, they blow out with a tiny pinhole to the concentric neutral they will have an open gap about 3/8" between primary and neutral. Need a good size DC pulse to jump the gap, then listen for the thump. Ours was $3K in 1994.
The 2273 is an excellent machine. I hate that they took the analog meter off and went totally digital with that machine. We have one of those also for the other office. I won't give up the 573.
You ever use yours for finding power lines at the 60 HZ scale and no transmitter?