You didn't answer the question of whether you have GFPE or GFCI protection.That’s the plan. I would also like to run it with no snow or ice on the roof
“ shoot low boys their riding shetland ponies”
GFCI will trip with only ~5 mA of leakage. GFPE will need 30, 50 or even 100 mA leakage depending on which unit is used.