Re: HACR Breakers
In the old days UL had special testing for circuit breakers to prove "...that the circuit breaker provided appropriate protection for the circuit components of typical heating, air
conditioning, and refrigeration equipment handle group motor applications..."
But now, since the 1990's, there is nothing special about the HACR rating.
According to Square D publication 0600DB0102:
"A great number of circuit breakers were investigated by UL using the special HACR testing. It was found that all circuit breakers that passed the normal UL 489 tests also passed the special HACR testing without a special design. As a result, UL 489 has been revised to recognize that all circuit breakers that satisfy
the construction and test requirements for UL 489 Listing are also suitable for HACR applications.
Paragraph 7.7 of the 9th edition of UL 489 grants HACR listing to all UL 489 Listed circuit breakers. There is no longer a requirement for special testing. These circuit breakers are suitable for group motor applications requiring HACR designation."