Re: Grounding
I am having a bit of trouble understanding what you have. Assuming a single 4,000 ampere switchgear with multiple disconnecting means, you will size the grounding electrode conductor for a 4,000 ampere service. Assuming up to six disconnecting means in separate enclosures, you will need a separate grounding electrode conductor for each.
In the second scenario, you are also permitted to run a single grounding electrode conductor and tap off of it to each individual service disconnecting means.