What is the minimum size wire to be used for ground rods. And code section
What is the minimum size wire to be used for ground rods. And code section
Article 250.66(A) and Table 250.66
@Old Man Moderator - Ok...im just teasing you now.....get your finger off the BAN button.....don't you do it.....doooonnn't you dooooo ittt !
Some say you can just land your ground rod number six onto the GEC at the cold water pipe 5'. Some say you have to bring it all the way to the BuSsbar
In belief, man can do anything
As Bob said #8 but that would require protection from physical damage so using #6 might be easier.
(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its enclosure
shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permitted
to be installed on or through framing members. A 4
AWG or larger copper or aluminum grounding electrode
conductor shall be protected if exposed to physical damage.
A 6 AWG grounding electrode conductor that is free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without metal
covering or protection if it is securely fastened to the construction;
otherwise, it shall be protected in rigid metal
conduit (RMC), intermediate metal conduit (IMC), rigid
polyvinyl chloride conduit (PVC), reinforced thermosetting
resin conduit (RTRC), electrical metallic tubing (EMT), or
cable armor. Grounding electrode conductors smaller than 6
AWG shall be protected in RMC, IMC, PVC, RTRC, EMT,
or cable armor.
I think almost all GEC to a ground rod (that I have seen) are subject to physical damage but have never turned an installation down.
If the water pipe is a grounding electrode then that is true. The conductor from the water pipe is the GEC, the conductor to the ground rod is a bonding jumper.Some say you can just land your ground rod number six onto the GEC at the cold water pipe 5'. Some say you have to bring it all the way to the BuSsbar
In belief, man can do anything
Since an unprotected #6 to the rod(s) is an almost universal norm I would say that most disagree with your assessment about physical damage.
I think the rod to soil connection is the weakest link in most instances.Rob
Any idea how many I see damaged/disconnected because of the individuals that mow/trim the yard?
IMHO the 'acorn' is the weakest link! Thoughts?
Any idea how many I see damaged/disconnected because of the individuals that mow/trim the yard?
IMHO the 'acorn' is the weakest link! Thoughts?
I have some thoughts, unless you are seeing rods longer than 8' you are seeing improper installations.
I have some thoughts, unless you are seeing rods longer than 8' you are seeing improper installations.
The rod and the GEC/bonding jumper should be invisible.