Ground Ring

Status
Not open for further replies.

Woodyz

Member
Installing new service for Horse boarding business. Thinking of installing ground ring and bonding at various places around metal building.

What are advantages-disadvantages to ground ring?

Wanting to protect livestock from any stray voltage or faults.

Will ground ring add better lightning protection?
 

drg

Senior Member
Re: Ground Ring

Member #22773 Ill pass along information where you can get obtain a "Agricultural wiring handbook "

National food and energy council
P.O. Box 309 2333 Rombach Avenue
Wilmington, Ohio 45177

Phone # 937-383-0001 Fax: 937-383-0003
www.nfec.org

The book would be the "13th edition published by the National food and energy council".
Its a 108 page handbook devoted exclusively to planning safe and efficient farm wiring systems.

lots of good information that you will want to know when working around AG. buildings and livestock.
 

bphgravity

Senior Member
Location
Florida
Re: Ground Ring

Put the animals in rubber boots and don't let them eat from the ground.

See article 547 for agricultural building installations.

There is no such thing as lightning protection.
 

drg

Senior Member
Re: Ground Ring

The "rubber boots" would help but not when a horse sticks his neck through a fence or gate to graze or drink and that metal section has stray voltage on it, he will get shocked probably in his mouth or neck.

If there is stray voltage problems on a farm the animals will just show you by simply avoiding the food or water in the area that has voltage present then you have to figure out the rest.......
 