Re: Ground Fault Protection - Immersion Heater
nhee,
We use heaters as part of a cooling product and I don't think the NEC clearly defines that application. It is not an appliance heater, Article 422, could be a fixed electric space-heating element, Article 424. However, these 3-phase are typically used where piping is heat traced, Article 427. Based on that we follow the GFP guidelines. I got feedback from a contractor in NC that states that is state law, at least in his words. It may be overkill, however I like what I have heard from others here, "the NEC is not a design manual it is a minimum safety standard."
Tony