Gronding at mobile home

Status
Not open for further replies.

dillon3c

Senior Member
Re: Gronding at mobile home

Charlie,
As long as the following conditions of 550.16(c) are met, then no, a driven electrode is not required for the metalic structure,but rather for service equipment itself.
 

dillon3c

Senior Member
Re: Gronding at mobile home

charlie,Lets back up a little bit,in your first post,you said "mobile home service"...250.32,Is two or more buildings or structures supplied from a common service.I'm confused on the intent of your installation...

----------------------------------------------------------------------------------------------*New to this post

Added:I had returned in searching, for this past thread..To see what my answer in reply, might have been from past..No then, No now..

*see 550.16,
dillon

[ August 20, 2005, 06:31 PM: Message edited by: dillon3c ]
 
Re: Gronding at mobile home

On a typical installation the service is remote from the trailer and I was just wondering if there should also be a ground rod at the trailer as it is not attached to the service and the primary purpose of a ground rod is for lightning??
 

trip

Member
Re: Gronding at mobile home

Goog question Charlie, I think he me means, do you treat it as a another building or structure, as in 250.32
 