brian ploskunak
Member
I have gas station that we are installing a permanent generator to run the whole store but not the car wash. What is the typical method for shedding loads? Shunt trip breakers or full voltage contactors?
don_resqcapt19 said:I agree with Steve. Just install an additional key interlock on the breaker that serves the car wash. Make sure that you check with the AHJ as to the use of key interlocks in place of a transfer switch. It should be ok, but some may have objections to it.
702.6
Don
kingpb said:If the Owner is willing to pay for a generator, I would convince him to install an ATS switch and set him up to do an auto transfer on power loss, and then return to normal service, without having to monkey around with making manual changes.
Do it right, do it once, and forget it.
brian ploskunak said:I'll probably go with a shut trip if the inspector doesn't go for the "LABEL". Thanks for all the input!
engy said:Is the shunt trip something the inspector can require? (I don't think so)
The generator is obviously not required for life safety.
Wouldn't it be purely a design decision how to drop the car wash load?
702.5 Capacity and Rating.
An optional standby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time. Optional standby system equipment shall be suitable for the maximum available fault current at its terminals. The user of the optional standby system shall be permitted to select the load connected to the system.
benaround said:How would you wire the shunt trip for the car wash when power is from
same bus bars?