If you
do not switch the neutral, the generator neutral must not be bonded to the generator case, and should not be re-grounded.
If you
do switch the neutral, (Separately Derived System) the generator neutral must be bonded to the generator case, and must be connected to an acceptable grounding electrode.
If the service has Ground Fault Protection, this configuration is recommended.
Ed