Thanks, I spent almost 2 hours looking for the problem then found unbonded issue, corrected and now it works fine, wanted to make sure i had actually found the problem
 

tom baker

First Chief Moderator
Staff member
I have seen similar on an ungrounded control power transformer. Your situation would have no fault current return path to generator windings for a line to ground fault
 