I'm a little confused on if this is allowed or not.
I'm installing a heater in a large enclosure. A 415V-3Ø, 42/21 kW heater was purchased, with those numbers being the high & low heater settings. 42kW is way too much for this enclosure and 21kW is the amount we need. Are we allowed to size our branch circuit breaker to the 21kW knowing that we will never turn it up to the 42kW setting? If we did, it will trip the breaker, stopping any additional issues. A sign will be placed on the heater to state its never to be changed to 42kW.
So in this case, installing a 40A breaker to limit it to the 21kW. In my opinion this is ok according to code because you are sizing the breaker to the continuous load current. It may not be the continuous full load of the equipment, but it is for our application on the low setting.
I'm installing a heater in a large enclosure. A 415V-3Ø, 42/21 kW heater was purchased, with those numbers being the high & low heater settings. 42kW is way too much for this enclosure and 21kW is the amount we need. Are we allowed to size our branch circuit breaker to the 21kW knowing that we will never turn it up to the 42kW setting? If we did, it will trip the breaker, stopping any additional issues. A sign will be placed on the heater to state its never to be changed to 42kW.
So in this case, installing a 40A breaker to limit it to the 21kW. In my opinion this is ok according to code because you are sizing the breaker to the continuous load current. It may not be the continuous full load of the equipment, but it is for our application on the low setting.