Gasoline resistant Cat 6

pmoney44

Member
Location
MASSACHUSETTS
Good afternoon,

I'm looking to see if anyone has any experience in whether gasoline resistant cat 6 is needed for gasoline Dispensers or can you just use regular cat 6? My argument to use regular cat 6 is that when each conduit enters the dispenser it is then rigid piped into said Dispenser. There isn't any wire exposed to the elements. Gasoline resistant cat 6 1,000' reel is $4,500. I know certain Dispensers have said requirements for cable/wire but I can't find anything. Wondering if this is a code requirement?
Thanks in advance!!!
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Whatever you do must comply with Section 501.20 and Table 514.3(B)(1), Line 1. Essentially, UL 87 dictates wiring inside the dispenser.

NOTE: Even inside the overall dispenser enclosure, the cables are “…exposed to the [flammable] elements.” This is because threads leak; they can handle an explosion, but can't block entry.
 