Going to keep is straight forward and simple.
I have a SolarEdge 6000H-US inverter (single phase, 120/240V) feeding a single family home, requiring an OCPD of 35A. Since we are doing a line side tap, we are using a fused disconnect to feed the main service panel, 60A Disco with a 35A fuse. The MSP has a rating of 150A.
Our one line calls for a 60A disconnect (understandable), but is calling for #6AWG conductors and a #6 AWG ground? Before hearing about 230.42 (B) and 230.79 A through D, we would have just used #10 AWG conductors with a #8 ground (minimum would be a #10), all THHN.
My question is:
Which is correct? Do these codes (230.42 B and 230.79 A-D) refer to the service disconnecting means as the fuse/breaker in these systems or the rating of the disconnect itself? Bonus: Would my ground be sized to 250.6/250.102(c)(1) based on the load of my inverter, or the load of the service feeding into the house, which is 150Amps max, or simply 250.122?
Thank you
I have a SolarEdge 6000H-US inverter (single phase, 120/240V) feeding a single family home, requiring an OCPD of 35A. Since we are doing a line side tap, we are using a fused disconnect to feed the main service panel, 60A Disco with a 35A fuse. The MSP has a rating of 150A.
Our one line calls for a 60A disconnect (understandable), but is calling for #6AWG conductors and a #6 AWG ground? Before hearing about 230.42 (B) and 230.79 A through D, we would have just used #10 AWG conductors with a #8 ground (minimum would be a #10), all THHN.
My question is:
Which is correct? Do these codes (230.42 B and 230.79 A-D) refer to the service disconnecting means as the fuse/breaker in these systems or the rating of the disconnect itself? Bonus: Would my ground be sized to 250.6/250.102(c)(1) based on the load of my inverter, or the load of the service feeding into the house, which is 150Amps max, or simply 250.122?
Thank you