The high school I graduated from (my old alma mater) has asked me to help in any way to upgrade their football field lighting. I am glad to help at least design the circuitry and installation; seems like all schools are looking for donations to save money. The lighting levels have already been engineered to achieve a 50fc average by the manufacture but I would like to verify my calculations.

There are a total of 4 light standards and 46 luminaires; I will be feeding the controller with 480V, 125A, and 3W circuit. One side of the field will have two light standards each with 11 luminaires and I am going to circuit these through a common existing underground conduit. The circuit is 480V 3W and the lamps are 1500W each and I am assuming a 90% power factor, I have calculated the farthest light standard as follows: I=P/(Ex1.73x.90) or 22=16,500/(480x1.73x.90) so my circuit is 30A=22x1.25. Distance is 550? therefore: VD=1.73xKxIxD/CM or 16.41 (2.2%)=1.73x12.9x22.08x550/16,510 as #8, this calculation reveals a 30A circuit with 3-#8?s are okay. I do have a few questions though.

Q1: If PF=Watts/VA do I have enough information above to arrive at this without simply assuming 90%?

Q2: Should I calculate the ?K? factor rather than plugging 12.9 for the conductor?

Q3: I will be combining two 3-phase circuits in an existing 1-1/2? underground conduit, with this I understand table 310-15(B)(2)(a) as I can now have an allowable ampacity for #8 at 80% of 50A which is 40A; isn?t this only applicable to my actual load 22A and not my circuit breaker 30A?
 

bob

Senior Member
Location
Alabama
Q1: If PF=Watts/VA do I have enough information above to arrive at this without simply assuming 90%?
I looked in my Hubble Cat. and they list their 1500 watt MH input wattage as 1610 watts.

Q2: Should I calculate the ?K? factor rather than plugging 12.9 for the conductor? K at 20C = 10.5. Using the 12.9 give you the worst case
condition.

Q3: I will be combining two 3-phase circuits in an existing 1-1/2? underground conduit, with this I understand table 310-15(B)(2)(a) as I can now have an allowable ampacity for #8 at 80% of 50A which is 40A; isn?t this only applicable to my actual load 22A and not my circuit breaker 30A?
You can use the 90C rating to derate from. Don't forget to upgrade your
EGC per table 250.122. Since the run is underground the conductor insulation must have a "W" designator.
 

adavey

Senior Member
Location
New York
To add to this further, is a "soft starter" applicable to this installation ???????? If so, is it based on the transformer size ?????
 