FMC conduit connected to PVC conduit

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can you provide more detail ?
With the proper fittings it should be allowable but things like grounding need to be taken into account.
How are they being joined ? What size conduits/circuit, etc ?
 

tom baker

First Chief Moderator
Staff member
Your answer would be in different sections No violation if FMC is allowed. See uses allowed in respective articles. The FMC will need connection at one end to a bonding conductor per 250.118
 
Last edited:

Ted1776

Member
Location
Orange County
Occupation
Building Official
Can you provide more detail ?
With the proper fittings it should be allowable but things like grounding need to be taken into account.
How are they being joined ? What size conduits/circuit, etc ?
20amp lighting circuit, 3/4" conduit joined by electrical tape :)
 