Fire Pump Motor

Status
Not open for further replies.

frank2004

Member
I am designing a power supply and feeder to a fire pump motor. The feeder size is ok for voltage drop at full load current. It is a long distance to the motor and at start up of six times FLC the voltage drop will be about 11% for the proposed feeder cable size. Although this VD is only for a short period I am concerned that the motor may have difficulty in supplying the necessary torque for the fire pump. Any comments?
 

bdarnell

Senior Member
Location
Indianapolis, IN
Occupation
Retired Engineer
695.7 specifies not more than a 15% drop at start and a 5% drop when running at 115% of full load. So, you are OK there Code-wise. I'd run it by the manufacturer of the pump motor just to get their blessing.
 