News letter email, I don't know how many times i have had to tell sparky to NOT put in more than 2 90's in a run and they still do it, maybe this will should be required reading for all sparky's engaged in systems piping. Below is the news letter email we all got just recently, wanted to post it here because it is sooo true!
Pull Boxes and Feedback From BICSI Instructor
Mike:
In the August issue of the EC&M you had a question that asked about how far apart to locate pull boxes in underground nonmetallic conduit.
I realize the NEC doesn't really address many of the problems relating to low voltage cabling (Data Telecom) in reference to pull boxes etc.
I teach a BICSI program directed towards the installation of the Data cabling. The references we use are the Telecommunications Distribution methods manual and the Telecommunications Cabling installation manual. The recommendation in the manuals is that a pull box be placed every 100 feet or where 2 90's have been placed. Pulling CAT6 or CAT5E cable is restricted to 25 lbs pulling force whether one or 10 cables are pulled. Keeping to this limitation can be very hard if long runs are involved or too many bends are in place.
Many times the Electricians will run the conduit for the installation and we find more than the two 90's. After doing a class with one of the IBEW's one of the electricians pointed out to me that by code they could have 3 90's before having a pull box. This started to clear up some of the problems I would see when looking at jobs. I always stress to the students when working with an electrical contractor to explain that with the pulling limitations on the cable we need the additional pull boxes, fewer bends, and if possible sweeping 90's to ease the pull.
BICSI has a very good website at www.bicsi.org. As more and more of the Electrical contractors are getting into the low voltage field the manuals would be of great benefit as a reference when doing work in that field.
I enjoy your column and read it each month needless to say it has provided me with some very valuable information.
Thomas E. Martin
BICSI instructor
Prime Communications
Omaha, NE
Pull Boxes and Feedback From BICSI Instructor
Mike:
In the August issue of the EC&M you had a question that asked about how far apart to locate pull boxes in underground nonmetallic conduit.
I realize the NEC doesn't really address many of the problems relating to low voltage cabling (Data Telecom) in reference to pull boxes etc.
I teach a BICSI program directed towards the installation of the Data cabling. The references we use are the Telecommunications Distribution methods manual and the Telecommunications Cabling installation manual. The recommendation in the manuals is that a pull box be placed every 100 feet or where 2 90's have been placed. Pulling CAT6 or CAT5E cable is restricted to 25 lbs pulling force whether one or 10 cables are pulled. Keeping to this limitation can be very hard if long runs are involved or too many bends are in place.
Many times the Electricians will run the conduit for the installation and we find more than the two 90's. After doing a class with one of the IBEW's one of the electricians pointed out to me that by code they could have 3 90's before having a pull box. This started to clear up some of the problems I would see when looking at jobs. I always stress to the students when working with an electrical contractor to explain that with the pulling limitations on the cable we need the additional pull boxes, fewer bends, and if possible sweeping 90's to ease the pull.
BICSI has a very good website at www.bicsi.org. As more and more of the Electrical contractors are getting into the low voltage field the manuals would be of great benefit as a reference when doing work in that field.
I enjoy your column and read it each month needless to say it has provided me with some very valuable information.
Thomas E. Martin
BICSI instructor
Prime Communications
Omaha, NE