bmazzara

Member
Regarding a ?BIRTHING CENTER? within a ?multifunction building? (517.1)
101 Life Safety Code and Florida Building Code classifies this ?building? as a business.
This existing building is to be remodeled and is currently wired without approved methods providing secondary or ?redundant? grounding. It is understood that the waiting rooms, corridors, bathroom, etc does not need comply with wiring methods in Article 517.13, but how about the three ?BIRTHING ROOMS? within this building. These rooms contain tubs to allow the baby to better ?slide? into this wonderful world.
Seems that 517.1 and 517.11 provides a good descriptive basis, but new local feedback seem to be pushing to permit regular wiring methods (no redundant ground) in the birthing area. Lets consider the birthing area within 6 feet from the tub and less than 7.5 feet above the floor, including receptacle and lighting outlets. This new local ?push? proposal not to mandate compliance with 517.13 is being sought to include dental care rooms, doctor examining rooms, vision and eye examining rooms, etc. here and other area?s such as patient exam rooms, where the total examining rooms are (101 Life Safety Code) three or less?
 

gjhustad

Member
According to NFPA 70 and NFPA 101 6.1.5.1, the definition of a health care occcupancy is the treatment of 4 or more persons and where these patients are incapable of self preservation. Meaning a single doctor or dentist or facility or building that is only treating 1-3 patients at a time is not classified as a health care occupancy rather should be classified as a business acccording to NFPA 101 (A.6.1.11.1)

The definition of a health care occupancy is simply defined in those articles:
a. treatment of more then 4 patients
b. patients mostly incapable of self preservation

Therefore doctors offices, dentist offices, outpatient treatment centers, birthing centers, etc. that treat less then 4 patients that are capable of self preservation are classified as BUSINESSES according to NFPA 101 (A.6.1.11.1) and are therefore subject to those requirements of the NEC (NFPA 70)
 