Hello,
Could you please help me figure out the exact size of the transformer that is back-feeding to the utility? Is the procedure similar to a typical transformer, or is there any factor that needs to be considered?
Three Phase Transformer Example: V = 208, I = 175; Therefore: kVA = (208 x 175 x 1.732) / 1000 = 63.05kVA; this calculates to 63+ kVA, thus we round up to a standard Three Phase size 75kVA.
Any reference or links for the calculation will be highly appreciated.