Re: eq gr
First, I think that #2 is too small. That will have more than 7% voltage drop. The calculation for the minimum size EGC is based on the ratio of the area of the conductor that would normally used for the 68 amp load and the increased size that was actually used. The EGC has to be increased by the same ratio. The code required conductor size for a 68 amp load is #4 and the EGC would be a #8. The #4 has 41,740 circular mils and the #2 has 66,360. 66360/41740 =1.59
This is the factor that we must increase the EGC by. A #8 has an area of 16,510 circular mils. 16,510(1.59) = 26,248.3 circular mils. This is the smallest EGC that is permitted for this installation. A #6 has 26,240 circular mils making it too small, so a #4 with 41,740 circular mils is the code required EGC.
Don