I know I'm over thinking this,ok I guess I'm having a hard time with how the e lights will work with the normal lights off the occupancy sensor I'm use to doing industrial work.can you make me understand this. I can hook it up like the diagram says no problem like I said I'm confused about the occupancy sensor controlling all the lights including the e lights when normal power is in operation,help me understand I know its simple its just not sinking in thanks
A good question. The occupancy sensor cannot be used on the normal power feed, since that would cause the elight to switch to the backup power source when the occupancy sensor timed out. Exactly the opposite of what is needed.
To do what you want, the elight would have to have three inputs:
1. The emergency power source, which must
not be switched.
2. The on/off input, connected to manual switch or occupancy sensor, but not necessarily providing power, depending on the design. This is the
normal switch sense in the Wattstopper unit.
3. Unswitched normal power so that the elight's logic can override the normal on/off input when the normal power fails and force the light on. This does not necessarily provide power to the light at any time, again depending on design. This is the
normal power sense input on the Wattstopper.
An alternate mechanism would provide power during normal operation from a switched normal power circuit, but whenever the emergency power circuit switched on the light would go on. The
Wattstopper does not work this way.
This also cannot be done when the backup power source is internal to the luminaire or ballast.