ELEVATOR SUMP PUMP

Status
Not open for further replies.

dannay

Member
Does the receptacle located at the sump pit (GFI protected ofcourse) have to be on a seperate C/B and branch circuit from a convenience outlet in the elevator machine room?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: ELEVATOR SUMP PUMP

The sump pump receptacle (single) does not have to be GFCI protected, see 620.85

Also read 620.24

Roger
 