JDB3
Senior Member
- Location
- San Antonio, Texas
A fellow electrician asked me to help him trouble shoot a house where the receptacles & switches were replaced. His initial concern was that there was no voltage hot to neutral for a vanity fixture. My old plug in tester indicated an open neutral. We found the receptacle where they "stabbed" the 12 gauge wire into the back of a receptacle (one of the neutrals was not connected). Another circuit indicated hot & ground reversed. We found a receptacle where the ground wires were separated (connecting the grounds solved the problem). At a GFCI receptacle for the kitchen: the black, white, & ground were wire nutted & caped off together (the was originally wired for 1 line in & 2 load sets of wires out). Other items as well!!
Is there a good tester that will correctly identify "correct polarity & open grounds or neutrals? Thanks. I am semi-retired & all of this sure had me trying to "think" again.