Electrical Unbalance

Status
Not open for further replies.

OBONE

Member
Location
York Region
Occupation
Electrician
As I stated , it had everything to do with the issue. Rods installed, problem solved. Tks for all your witasism, what is the ground rod used for??
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As I stated , it had everything to do with the issue. Rods installed, problem solved. Tks for all your witasism, what is the ground rod used for??
It's not a substitute for an intact service neutral conductor. :confused:
 

OBONE

Member
Location
York Region
Occupation
Electrician
Maybe ask Sparky he seems to know all the answers.
I dont know the theory behind this, just happy the problem is fixed
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As I stated , it had everything to do with the issue. Rods installed, problem solved. Tks for all your witasism, what is the ground rod used for??
Sorry but even if it temporarily solved the problem it did not do so correctly. A grounding electrode has nothing to do with an open neutral issue. Don summed it up perfectly:
A connection to earth will never solve any electrical problem. In some cases it may mask the problem, but it will never solve the problem.
 
Status
Not open for further replies.
Top