kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
The house is three years old, and therefore under the 2002 Code. The code allows 10 receps @ 180VA per yoke on a 15A circuit. But, there are also 2-switches in each of two rooms that control separate ceiling light and fan functions. The switches are also on the same 15A circuit as the 10 receps.
What I cannot find is, what wattage for each of the ceiling light boxes should be used for the calculation. I doubt the fans w/lights were installed at the time the Contractor turned the house over to the Owner's, so, it probably had a standard 60W fixture in each room. But, since there are two switch legs going to the fan, the potential is there for two utilization devices. So, should I use 60W x 2 x 2, or just 60W for each outlet box? Either way, I know the circuit does not meet Code, just trying to determine exactly by how much, before I complain to the AHJ.
What I cannot find is, what wattage for each of the ceiling light boxes should be used for the calculation. I doubt the fans w/lights were installed at the time the Contractor turned the house over to the Owner's, so, it probably had a standard 60W fixture in each room. But, since there are two switch legs going to the fan, the potential is there for two utilization devices. So, should I use 60W x 2 x 2, or just 60W for each outlet box? Either way, I know the circuit does not meet Code, just trying to determine exactly by how much, before I complain to the AHJ.