Sorry, Dennis, but I disagree, from two perspectives. First and foremost, the manufacturer of the GFCI device might have published a limit on the downstream load. If so, then that would govern the installation.
Secondly, and this has been debated on this forum, at length, more than once already, but I continue to assert that there is no limit to the number of receptacles you can put on a 20 amp circuit, regardless of whether you are talking commercial or residential. My basis is that nothing in 210 calls upon you to invoke the load calculations within 220, in the design of your branch circuits.