I am having trouble finding where the code allows the use of Drop Cords the way we use them here in the plant I work at. I inherited this situation so I am trying to find where it tells me specifically how we can use these. Article 400.7(a)(6) is where it all started being use here but I am uncomfortable with the way we use it. The cords are 480 3 phase and from a bank of fused disconnects on one wall are fed to the other end of the 'room' via overhead conduit, then from a junction box at the end of the conduit run is spliced into SO cord and dropped with a wire mesh cord grip from the ceiling supporting members. The cord connector at the end of this hangs about 6 feet off the floor. The machines are plugged into these. There are several cords of varying voltages for different pieces of equipment. Few of them are ever actually moved in and out. Most of them stay in place for months or years. Are we stretching the permitted use a bit too far? And if not, is this otherwise properly constructed?