Double poll breakers

Status
Not open for further replies.

rdimase

Member
A question was raised as to the proper use of a double pole breaker, for a single 120 circuit. In one of our machines a Square D 2 pole 30 amp breaker was installed, with only one leg used for the circuit. I do not know why they did this but they did. Square D literature says the breaker will trip on overload on either leg and mentions that if a 120 volt circuit is used to use the posts by the trip indicator. I am Just wondering if the NEC addresses this anywhere. Seems like this is legal to me.
 

tom baker

First Chief Moderator
Staff member
Re: Double poll breakers

Is this a listed machine? If so then the listing would account for the double pole breakers, if its shown on the drawings then it would be allowed. It may not be a NEC issue at all, as it depends on what the machine is.
 

rdimase

Member
Re: Double poll breakers

Not sure whether it is listed or not. The breaker is depicted in the drawings and the equipment is a US Postal Service mail processing machine. Runs letters through it for processing.
 

sparkmantoo

Member
Location
Virginia
Re: Double poll breakers

i don,t see anything wrong with it. it is a common trip breaker put in by the manufacturer. i see alot of this where i work but it is from machines built in europe. they use three pole brkrs for single phase feeds. it think it is a cost issue too.
 

templdl

Senior Member
Location
Wisconsin
Re: Double poll breakers

If I understand you correctly a 2p common trip breaker was installed but one pole is only being used to feed a 120v load. If so there is no problem. A bit odd as a single pole would normaly be used but 1p of a 2p breaker will work just fine. Maybe they only had a 2p breaker available at the time of the installation.
 
Status