I have two jurisdictions wanting a second bore 12" above a bore feeding the meter/disconnect and warning ribbon installed. I say according to
300.5(D)(3) (Service Conductors. Underground service conductors that are not encased in concrete and that are buried 450 mm (18 in.) or more below grade shall have their location identified by a warning ribbon that is placed in the trench at least 300 mm (12 in.) above the underground installation." it is not required.
The key part being "shall have their location identified by a warning ribbon that is placed in the trench". Except at the tie in at either end there is no trench, therefore, no ribbon is required above the bore. Any comments for or against would be appreciated.Thanks
[ March 06, 2004, 03:59 PM: Message edited by: kurrent ]
300.5(D)(3) (Service Conductors. Underground service conductors that are not encased in concrete and that are buried 450 mm (18 in.) or more below grade shall have their location identified by a warning ribbon that is placed in the trench at least 300 mm (12 in.) above the underground installation." it is not required.