Every individual installation has it's own set of circumstances that may or may not make this system favorable, and you need to factor into those circumstances whether it is a full or open delta and if conditions on primary side are factor in this, particularly the open delta option. If primary situation is somewhat limiting to only using open delta you can increase transformer sizes if the load would dictate so.
Basically there is no simple answer. If all three primary phase lines are available and the majority of loading is 120 volt loads then that is about the only time a wye secondary is pretty much a must.
The only reason for the open delta is to provide three phase power while the replacement transformer comes in to complete a closed delta config. 120V loads make up less than 3% of a single transformer's kVA rating (the bank consists of three equal, well two at the moment, units). As such, your answer is a sigh of relief.
Center-tapped deltas have their purpose and it seems to fit the bill here. I was just somewhat confused as there is so much information out there calling for the avoidance of it, so much so that the POCO's manual goes into great detail as to how to set up a delta-delta (center-tapped) substation yet goes on to finish off the several pages long section with, and I kid you not, (word for word) "This type of connection doesn't serve much purpose, but it does have its application".
Mind you, this is an extremely technical document covering all sorts of things, from pole fixture installations to substation wiring, grounding patterns and mesh requirements, everything down to the last millimeter. I can't find any other instance of a similar comment or description. Yes, there are recommendations as to using this vs that, etc but it just so happens that the delta-delta connection part, despite being clearly included in the document and very well detailed, finished off with something of a "not sure why we're even covering this". This, in great part, is what sent me on this quest to figure out why there is no love for the double D. Imagine my reaction when I see that statement, which, at least to me, despite probably being "technically" correct, sounds so out of place in a manual that is entirely focused on detailed diagrams, schematics and instructions; almost entirely void of comments or observations.