Derating Feeders

Status
Not open for further replies.
J

jonny1982

Guest
Do (3) phase feeders have to be derated?

For instance, If I had a (3) phase 225 amp panel I was installing in a commercial application, could I use 3/0 copper. Lets say they where in emt conduit.
Wouldn't I have to derate at 80 percent since there will be 4 current carrying conductors in the pipe?

Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
Do (3) phase feeders have to be derated?

For instance, If I had a (3) phase 225 amp panel I was installing in a commercial application, could I use 3/0 copper. Lets say they where in emt conduit.
Wouldn't I have to derate at 80 percent since there will be 4 current carrying conductors in the pipe?

Thanks

Even without dearting you would need 4/0 copper for 225 amps.

You most likely will not have to derate unless the majority of the load is 'non-linear' which would be computers, electronic ballasts etc.

Follow Dave's code reference.
 

ron

Senior Member
You most likely will not have to derate unless the majority of the load is 'non-linear' which would be computers, electronic ballasts etc.

The need to count the neutral as a CCC, is a tough one to enforce. Almost all lighting in new commercial construction is a majority of non-linear lighting (fluorescent or LED) and most receptacles are used for PC's or VFD's.
 

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
I don't know what actually 310.15 says on that but in IEC the multi conductors cable has three different ampacities based on three different installations for (Free air, ducts, underground), and so you don't need any group derating based on the selected installation.
 

Smart $

Esteemed Member
Location
Ohio
I don't know what actually 310.15 says on that but in IEC the multi conductors cable has three different ampacities based on three different installations for (Free air, ducts, underground), and so you don't need any group derating based on the selected installation.
Being he's in the US, I doubt he's installing per IEC. ;)
 

iwire

Moderator
Staff member
Location
Massachusetts
I don't know what actually 310.15 says on that but in IEC the multi conductors cable has three different ampacities based on three different installations for (Free air, ducts, underground), and so you don't need any group derating based on the selected installation.

We have different ampacities for those as well that still does not let us escape derating when more than three current carrying conductors are run together.
 

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
That makes sense particularly for those non-linear loads.
 
Status
Not open for further replies.
Top