DC source circuit conductors inside wall?

Status
Not open for further replies.

Zee

Senior Member
Location
CA
Can I run DC source circuit conductors, in EMT, inside wall?
Does it change things if it's optimizers?
How about rapid shut down?
DC Disco on roof?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Can I run DC source circuit conductors, in EMT, inside wall?
Yes.

Does it change things if it's optimizers?
Maybe it changes the nitty gritty of some code requirements (technically that's not a source circuit anymore), but you can still do it.

How about rapid shut down?
Doesn't change anything.

DC Disco on roof?
Doesn't change anything.
 

Zee

Senior Member
Location
CA
thx

To be clear: no provisions must be made to de-energize the conductors if inside wall?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
thx

To be clear: no provisions must be made to de-energize the conductors if inside wall?
The NEC does not require it of PV source circuits but your AHJ might. But 690.15(C) says that if you combine strings on a roof you must have a disco up there.
 