DC Disconnect between Solar Panels and Inverter

Status
Not open for further replies.

Orion2021

New User
Location
Nebraska
Occupation
Electrical Contractor
Is it, and if yes a code reference please, required to install a disconnecting means between DC solar panels (400 volt 30 amp with Rapid Shut Down devices on each panel) and the inverters which are located 60 feet away? My AHJ is operating under 2017 NEC currently.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Yes, but if there is a disconnect in the inverter, as is typical, then that normally meets the requirment and most likely there is no requirement for an additional disconnect. You just have to use metal raceways if running through the building.

The distance is irrelevant.

See 690.15, 690.15(A) and 690.31(G).
 