CSST gas line bonding

Status
Not open for further replies.

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Isn't the bonding easier to do if it originates outside anyway? Just run up from the house side of the meter, then either along the eaves or into the attic. Come out of the attic and down at the Service Equipment. Connect either to existing outside electrodes, at Intersystem Bonding means, or into Service Disconnect.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Isn't the bonding easier to do if it originates outside anyway? Just run up from the house side of the meter, then either along the eaves or into the attic. Come out of the attic and down at the Service Equipment. Connect either to existing outside electrodes, at Intersystem Bonding means, or into Service Disconnect.

That would give a good path for AC fault current, one purpose of bonding, but would be so roundabout a path that it might have little if any effect on lightning-induced current. (Not necessarily a direct strike.)
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Isn't the bonding easier to do if it originates outside anyway? Just run up from the house side of the meter, then either along the eaves or into the attic. Come out of the attic and down at the Service Equipment. Connect either to existing outside electrodes, at Intersystem Bonding means, or into Service Disconnect.

Attic work is difficult unless you are talking new construction. The gas meter is normally in close proximity to the service entrance equipment so tying into the GEC with a jumper to the CSST or black pipe at the meter is the ticket.
 