continuous grounding conductor

Status
Not open for further replies.

rsimp1967

Member
Location
Indiana
Is it a separatly derived system if a continuos grounding conductor is present from 480 volt panel to the transformer to the low voltage panel?

[ April 07, 2003, 10:42 PM: Message edited by: rsimp1967 ]
 

Ed MacLaren

Senior Member
Re: continuous grounding conductor

If by "continuous grounding conductor" you mean an equipment grounding conductor, the answer is yes.

In the sketch, the 208/120 volt system is a Separately Derived System (SDS).

Trans4.gif


Ed

[ April 07, 2003, 10:59 PM: Message edited by: Ed MacLaren ]
 

bennie

Esteemed Member
Re: continuous grounding conductor

Ed: Is the padmount transformer a separately derived system?
 

Ed MacLaren

Senior Member
Re: continuous grounding conductor

Is the padmount transformer a separately derived system?
I suppose it depends on one's definition of what an SDS is.

The padmount transformer in the sketch above supplies the 480 volt building service (System 2). My "interpretation" of the SDS definition is "a system that derives it's energy from a source other than the building or facility's service", so to me it is not.

However, the 480 volt system (service) is definitely "derived separately" from the 7200 volt distribution system. (System 1)

So if the 7200 volt system was the service to the facility, than System 2 would be an SDS.

Ed

[ April 10, 2003, 07:40 AM: Message edited by: Ed MacLaren ]
 

bennie

Esteemed Member
Re: continuous grounding conductor

A service to a premises can only be supplied, or derived. This is an accepted engineering standard.

Are you saying the padmount is a supplied source, and the user end transformer is derived from a source?

[ April 10, 2003, 01:10 AM: Message edited by: bennie ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: continuous grounding conductor

Bennie,
The primary to both transformers are "supplied sources". The secondary side of both transformers are "derived sources". The 'derived source'(secondary side) of a transformer becomes the supply source for all the equipment served by that transformer, including any additional transformers.
Don
 

bennie

Esteemed Member
Re: continuous grounding conductor

Don: Is that description from one of the Stallcup publications?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: continuous grounding conductor

Bennie,
Thats not from any source that I know of. It is just how I read the code.
Don
 

bennie

Esteemed Member
Re: continuous grounding conductor

Don: Does the code permit grounding the X-O of what is being called a separately derived system, at the building ground, as shown in the schematic?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: continuous grounding conductor

Bennie,
The code requires that the grounding electrode for the transformer be as near as practicable to and preferably in the same area as the transformer. The service grounding electrode could be used for this. In any case no matter what electrode is used at the transformer it is bonded to the service grounding electrode.
Don
 

gwz2

Senior Member
Location
Indiana
Re: continuous grounding conductor

The way I read bennie's last post was questioned if the Xo of the SDS ( the right-hand transformer in Ed's diagram ) could be connected to the building ground.

Assuming he meant "effectively grounded structural metal member of the structure" as in 250.30(A)(4)(1), yes , that is the first choice per the 2002 NEC.

The actual connection to the Xo can only be done at the same point as the bonding Jumper of 250.30(A)(1) [ last sentence ] or as per 250.30(A)(2))(a) [ last sentence ].

Glenn
 

gwz2

Senior Member
Location
Indiana
Re: continuous grounding conductor

And, the "effectively grounded structural metal member " is required to be grounded to the Service Equipment as per 250.50 or 250.104(C).

Therefore, as Don noted, it is grounded to the service grounding electrode.

Glenn
 

bennie

Esteemed Member
Re: continuous grounding conductor

On a wooden building the transformer is 150 feet from the service. Do you drive two ground rods to ground the transformer?
 

bennie

Esteemed Member
Re: continuous grounding conductor

Effectively grounded structural members are bonded only if there is a low impedance ground ring around the building. Each structural member must be welded to the ground ring.(Shorted)

There is not many buildings with effectively grounded structural members, bonded to make one electrode.

When the ground for a transformer ends at the building ground, why not go there direct?
 

bennie

Esteemed Member
Re: continuous grounding conductor

Someone please explain how a transformer, if part of listed service equipment, can be connected to the building ground electrode?

A transformer one foot away from the listed equipment must be connected to a structural member or water pipe.

This is nonsense, and only shows the popular understanding of a separately derived system, is hogwash.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: continuous grounding conductor

Originally posted by bennie:
Effectively grounded structural members are bonded only if there is a low impedance ground ring around the building. Each structural member must be welded to the ground ring.(Shorted)

There is not many buildings with effectively grounded structural members, bonded to make one electrode.
In a building with a steel "skeleton" how are these members not bonded, they are either welded or bolted solidly together (one would hope :D )

However a lot of the buildings we do here have a grounding ring with the building columns cad welded to the ring.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: continuous grounding conductor

Bennie, do you have access to the 2002 handbook? If so look at exhibit 250.15. It shows the wooden frame building you are referring too. If you do not have a copy it is simple a common ground electrode cable that starts at the water pipe and rises through the structure in which each transformer is bonded via "H" tap.

Although the buildings I work with are steel frame or poured concrete structures, exhibit 250.15 is precisely how I have been treating transformers for years. It forms the single point ground and prevents common mode current sort of. I say "sort of" because unless you isolate the raceways and equipment from incidental contact from the building structures like concrete, framework, and rebar-it is not really single point anymore. No one goes to that kind of trouble except some specialized industries.

Before anybody blast me about going to building steel or pipe nearby I do, but the primary path is dedicated to the building electrode system.
 

bennie

Esteemed Member
Re: continuous grounding conductor

Bob: Do you think the rusted, painted, monocoat covered, loose, steel makes a credible ground electrode, when splices are not permitted in a ground electrode conductor?

Would you think the steel makes a better electrode when the building electrode is the same distance or less.

The grounding requirements, for a separately derived system, were written when the premises wiring system did not have a ground electrode system.

This is why there is no reference to the building ground, it did not exist at the time.
 

bennie

Esteemed Member
Re: continuous grounding conductor

Dereck: You are correct, except for mentioning the equipment ground conductor from the building ground to the secondary of the transformer.

When current is on both the building ground, and the transformer ground, there will be common mode voltage between the neutral and ground. They both terminate at the water pipe, but originate at different locations.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: continuous grounding conductor

Bennie, It is a system that seems to work just fine, after all along with building steel you also end up connected to the equipment grounding conductor.

I know you are going to say something about parallel paths and I will not pretend to understand all of the intricacies of this like "common mode current", but for the literally hundreds of thousands buildings done this way and the limited problems arising it seems like it works.

As I asked you before how would you like to see it done, forgetting about the NEC?
:)
 