I have two inverters with max. output ea. of 41.6A. So, 83.2A, but 104A with continuous duty.
A non-fused AC disconnect is rated at 100% for continuous duty, so i could use a 100A disconnect. (as long as my wire is rated for the 104A)
But when i get to the interconnection breaker at the MDP, I need to be at 110A. right?
So, impso-facto... can i even use a 100A disconnect if the intertie breaker is 110A?
It seems to work, until you look at it in reverse feed.
~m
A non-fused AC disconnect is rated at 100% for continuous duty, so i could use a 100A disconnect. (as long as my wire is rated for the 104A)
But when i get to the interconnection breaker at the MDP, I need to be at 110A. right?
So, impso-facto... can i even use a 100A disconnect if the intertie breaker is 110A?
It seems to work, until you look at it in reverse feed.