Recently I started a thread about moving the RF meter from the house to the POCO service pole.
Four 4/0 al conductors for source and load are under the 40% fill for 2". I would add a 2/0 Al for the grounded conductor only because of the wire available. This conductor takes the fill over 40%.
Should it even count since it will stop at the new meter socket and there will be no panel below the meter?