Is it allowable to use the 90 degree rating instead of 75, when calculating the conductor size using the 25' tap rule? One end is terminated directly to busing, and the other to a breaker.
I belive that UL standards for molded case breakers and fusible switches do not allow 90C at the terminals. 100% rated equipment requires 90C conductors sized at 75C.