While inspecting a 120/240 v, 1-phase, 400 amp service, I found the #4 concrete encased electrode connected to a lug "outside" the metal enclosure of the main disconnect.
I failed the inspection citing article 250.24(A)(1) stating: the connection shall be inside on the equipmemt/grounded bus bar.
My fellow electrical inspectors felt that the aritilce did not preclude an exterior CEC connectiion, if all other servioce groudning ok.
What do other professionls think??
I failed the inspection citing article 250.24(A)(1) stating: the connection shall be inside on the equipmemt/grounded bus bar.
My fellow electrical inspectors felt that the aritilce did not preclude an exterior CEC connectiion, if all other servioce groudning ok.
What do other professionls think??