Cold Water Bond

Status
Not open for further replies.

amend15

Member
Location
California
Occupation
Electrician
Hello I’m doing a commercial building, in which we are putting a new service switchboard from the transformer. The cold water entrance to the building is on the complete opposite of the building. Does the bond have to be within 5feet of the entrance of the cold water pipe into the building? Or are we allowed to bond to the cold water wherever is closest to the MSB?
Thanks
 

tom baker

First Chief Moderator
Staff member
If metallic watet line qualifies as a grounding electrode, ten feet in contact with the soil, the grounding connectiom is made within 5 ft of entrance. If not the bonding connectoon van be made anywhere, but both must be accessible.
 