Clearances from Customer Owned XFMR to Building

Status
Not open for further replies.

Tiki1469

Member
Location
USA
Occupation
Contractor
We are installing a customer owned <500gal mineral oil XFMR with 13.8 primary on a concrete pad outdoors.

What is the clearance from the side of the metal building (locked entrance property) to the side of the XFMR (non-access side, non-cooling side)?

From what I understand from reading 2023 NEC and browsing this forum, this seems to be an insurance and/or, more probably, an AHJ concern more than an NEC concern.
 

Opie11

Member
Location
New York
Occupation
Railroad Electrician
I am assuming a service?
Just installed something similar. Utility dictated clearance of transformer and neighboring buildings/obstacles.
FWIW we had to have 3' all the way around.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
We are installing a customer owned <500gal mineral oil XFMR with 13.8 primary on a concrete pad outdoors.

What is the clearance from the side of the metal building (locked entrance property) to the side of the XFMR (non-access side, non-cooling side)?

From what I understand from reading 2023 NEC and browsing this forum, this seems to be an insurance and/or, more probably, an AHJ concern more than an NEC concern.
See here. Informative and manufacturer recommended.
 