Excellent explanation thank you. To tie it back to the main discussion, the isolated ground is in fact a reference wire to the bond, not a graounding wire because of the above.
There are many "theories" on the reason for and application of IG circuits. From what I recall, the reason IG's are permitted in the NEC is none of the above. Everything mentioned so far in this thread can be served with solid, redundant, and low-resistance grounding methods, including providing a steady-state voltage reference.
The NEC initially permitted isolated grouunding for the purpose of mitigating RFI/EMI. Older electronic gear emitted a lot of RFI compared to modern equipment. In order to mitigate widespread RFI, shielding techniques were employed in the equipment. Just as many communications wires are shielded to prevent influence from external stray signals, the same rationale also serves to mitigate the external spread of RFI generated from within. The [conductive, metal] shielding utilized in that equipment was connected to ground.
Going back in time a bit more, it was tied to the neutral upon the advent and use of the polarized two-prong plug and receptacle. Any of you ever opened up an old tube-type TV or amplifier? What wiring could be, was done so within the "chassis", a prime example of shielding to mitigate the spread of RFI.
The one application which has been correct thus far is "ALL IG CIRCUITS SHOULD BE INSTALLED IN METAL CONDUIT". The reason is, it has been found that connecting the equipment shielding to any conductor can in effect cause it to act as an antenna, which is actually the opposite of all intents and purposes. Running the IG circuits in metal raceway (i.e. includes metal conduit and tubing
) acts to shield the IG "drain" wire. There is no requirement for running IG circuits in metal raceway, but if using a non-metallic wiring method, that is taking the risk of having an antenna-effect IG wire.
Wrong or right, you guys now have my two-cents worth on the matter. :angel: