Chlorine

Yukon Jake

New User
Location
Alaska
Occupation
Electrician
We are working on a Building and installing a new pool system. This Chlorine room has EYSs and a lot of work that was done after the fact by Maintenace I'm sure.

Where does chlorine fall under in the NEC code, (Hazardous Locations)? In the SDS it says it May cause or intensify fire; oxidizer.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
In the forms and concentrations that you're dealing with for a pool, it is unlikely that you have a hazardous location as far as the NEC is concerned. The NEC is more concerned with the presence of fuel, and not oxidizers, medical gases excepted.
 

NoahsArc

Member
Location
Illinois
Occupation
Residential Electrician
There's 680.14 in 2020, which directs to 680.2:Corrosive Environment, which to me would clearly include any "chlorine room". 680.14 requires wiring methods to be listed for such use, which includes explicitly RMC, IMC, and rigid PVC, and RTSC
 
Top