OK,so a 20 space/20 circuit load center will physically not allow the use of a "cheater" breaker. So it won't allow a 15 amp cheater but what's to stop me from installing a 30 amp double pole?
I think a cheater breaker is a piggy back or twin breaker
I think a cheater breaker is a piggy back or twin breaker
And what is CTL?
- Close The Loop?
- Can't Tell a Lie?
- Constantly Turning Left?
- Chamomile Tea Lover?
- Chance to Teach a Lesson?
- Complete Two Laps?
And LeeLee, that brings us back to the question of what you plan to do with the 2-pole 30 amp breaker, and how you are anticipating that it will resolve your present concern.
I believe manufacturers make non-CTL tandems that'll fit in CTL panel spaces. Using one (or more) where not rated for tandem breakers would be a panel listing violation.
Not at all. The whole rationale underlying OCPD under the NEC is that where the loads are predictable (calculable), the contribution of each circuit to the load on the panel bus is just the calculated load which is going to be on that circuit.Golddigger,
"It probably originally had both fill-factor type safety concerns and simple marketing concerns."
.....and that is another concept I haven't grasped. If you fill a 30 space,150 amp load center with 30 15 amp breakers,haven't you theoretically "overloaded" the load center by 150 amps? Even so,big deal....isn't it the job of the main breaker to protect everything?
Funny you mention AFCI's. They are the whole reason I had to install the sub. My main was full and resorted to some tandems. I wanted to upgrade to all AFCI's but since they don't make a tandem AFCI,I had to get rid of the tandems,hence the need for a sub. Anyway,it seems like the 30 amp 240V circuit will be fine in my sub. Thanks to all for your help.