Can you connect two seperate ground cables to one ground pipe?

Status
Not open for further replies.

bklynchris

Member
Location
brooklyn ny
This home has two electric meters with two fuse boxes.
One fuse box has #4 copper in bx cable connected to the copper water pipe about two feet above were it enters the house.
This copper water pipe is buried ten feet in the ground.
The other box is not grounded.
Can this box also be connected to the same water pipe?
Home is in Brooklyn NY
Thanks
 

bklynchris

Member
Location
brooklyn ny
This home has two electric meters with two fuse boxes.
One fuse box has #4 copper in bx cable connected to the copper water pipe about two feet above were it enters the house.
This copper water pipe is buried ten feet in the ground.
The other box is not grounded.
Can this box also be connected to the same water pipe?
Home is in Brooklyn NY
Thanks

anyone know the answer?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes you can connect 2 grounding electrode conductors to the same water pipe within 5' of where it enters the building but you must use separate ground clamps.
 