Presently two dwellings on the property sharing a 200A post-mount Mobile pack (meter/main). Larger house off the 200A feed-through lugs, smaller off a 100A 2P breaker.
Adding a 100A mobile-pack on the back of the same post to dedicate to the smaller dwelling so they can have their own utility bills. Can I splice onto the 100A feeder residing in the 200A enclosure and run it into the new panel via PVC nipple joining the two? Or do I have to disconnect the 100A raceway entirely and swing it over to the new panel.
Adding a 100A mobile-pack on the back of the same post to dedicate to the smaller dwelling so they can have their own utility bills. Can I splice onto the 100A feeder residing in the 200A enclosure and run it into the new panel via PVC nipple joining the two? Or do I have to disconnect the 100A raceway entirely and swing it over to the new panel.