I have a Bulldog panel with pushmatic breakers. With main and sub bus bars. There are the 2 hots coming in from outside into the box and connected to the bus bar. there is no main shutoff. There are 3 30amp dbl pole breakers at the top of the bus bar which are used for furnace, electric stove, etc. There is a 50amp breaker that connects the upper bus bar to the lower bus bar. the rest of the lower bus bar has 15 and 20 amp breakers.

the 50 amp breaker is failing to stay energized, there is a replacement from Connecticut electric For the same breaker. however the only way to remove the 50 amp breaker is to unscrew 2 screws on the hot bus and 2 screws on the lower bus which is hot, I have no way to shut of power to the box, other than calling an electrician.

question: using a dual insulation screw driver rated for 1000 volts and wearing a pair of class 0 rubber linesman gloves, would it be stupid to remove the 4 screws replace the breaker and screw it back in?

in the past I’ve shut the 50 amp off to the lower section to replace breakers and added a new circuit while tlhe box is hot, but never directly worked on a bus that was hot.

just need to hear from some experts as to my thinking.
thank you.

Zig
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Get an electrician before you get hurt

This site is designed for:
  • Electrical Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
Status
Not open for further replies.
Top