What is the box fill calculation for 6-2" pvc conduit each having 9 #2 Thhn feeders and 3 #6 grounds (total of 27 #2 splices and 9 #6 splices). there are no bends (straight through splices) and the box is pvc.
 

bphgravity

Senior Member
Location
Florida
Re: Box Fill

For these type of questions, it is best that you provide your calculations so we can respond and assist. Start with section 314.28 of the 2002 NEC. :)

HINT: The conductors play no role in this particular type of box sizing calc. ;)

[ June 21, 2004, 01:54 PM: Message edited by: bphgravity ]
 

ncjohn

Member
Re: Box Fill

There is a good article written Mar 1, 2004 by Mike Holt in the EC&M Magizine called "Size Does Matter"

Search for that and hopefully you will be able to figure out your answer.

If you need any help with your calculations let me know.

-------------
John Lemire, EI
Design Engineer
 