I have 6 # 10s THHN coming into a4X4x2 1/4 J box through a 3/4 EMT. I have two 2 wire MC cables coming into this J box also,that makes 12 # 10s. 4 black,4 white,4 green. Can I add anymore, would I need a bigger box to add a circuit or a box extension?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have 6 # 10s THHN coming into a4X4x2 1/4 J box through a 3/4 EMT. I have two 2 wire MC cables coming into this J box also,that makes 12 # 10s. 4 black,4 white,4 green. Can I add anymore, would I need a bigger box to add a circuit or a box extension?


According to T314.16(A) you're allowed 12-#10 conductors. Did you do a calculation?
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I have 6 # 10s THHN coming into a4X4x2 1/4 J box through a 3/4 EMT. I have two 2 wire MC cables coming into this J box also,that makes 12 # 10s. 4 black,4 white,4 green. Can I add anymore, would I need a bigger box to add a circuit or a box extension?

Don't the Equipment Grounding conductors, green, only get counted once?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
In terms of ampacity, none of them count. In terms of conduit or box fill, they all take up space. Bare EGCs take less space than insulated ones would.

Sent from my XT1080 using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
All of the EGC's count as one single conductor for box fill. There is no distinction made in 314.16(B) for bare or insulated conductors.
 

Smart $

Esteemed Member
Location
Ohio
In terms of ampacity, none of them count. In terms of conduit or box fill, they all take up space. Bare EGCs take less space than insulated ones would.

Sent from my XT1080 using Tapatalk
But according to box fill requirements, all EGC's count as one "volume" using the largest of the lot. Each additional set, such as isolated EGC's, count as one additional "volume".

OP has 9 "volumes" of box fill at 2.5 in? each [unless he failed to enamor any I-EGC(s)]. That's 22.5 in? total. OP said 2-1/4 deep 4sq, but 2-1/8 deep is standard at 30.3 in?. He has room for 3 more #10 volume allowances.
 